CSV-A8

Does the CSV-A8 have to be installed on a bare conductor, or does it simply clamp on to an insulated conductor wire?
Associated Product 

Comments & Subscriptions


 

The CSV-A8 can clamp on to either a bare or insulated conductor wire, as long as that wire is a single "hot" line.
Cheers,
Gregg

A follow-up question: It seems the CSV-A8 cannot be calibrated to Alarm on Overcurrent *and* also be used with a data logger to record normal operation closing/opening? Is this a correct observation? Thanks.

You are correct. The CSV-A8 is designed simply for on/off recording. Feel free to reach out to our Sales Applications Team (sales@onsetcomp.com) for other options for alarming on over-current.

Cheers,

Gregg

WHEN YOU SAY IT MEASURES A SINGLE HOT WIRE DOES THAT MEAN ONLY ONE PHASE OR CAN IT FIT OVER THE POWER CABLE TO A MOTORIZED HAND DEVICE PLUGGED INTO A 120V RECEPTICLE? THANKS.